Backslope and drainage in a sewer line! Professional opinions.......

This site may earn a commission from merchant affiliate
links, including eBay, Amazon, Skimlinks, and others.

Joined
Nov 16, 2004
Threads
64
Messages
1,203
Location
NRV of Virginia
Well after living in the same house since 1998 we had the first sewer line backup, thankfully not a bad one (if that is possible). I have one spot that has a little sag in the main line, water is sitting in that spot. We confirmed this with a camera and other than that one spot he says it all looks good.

Got a question for the plumbers out there, is it possible to cut about two inches out of the vertical lines(black plastic pipes), connect them with fernco's and create a little more slope. The plumber said it could/should take care of the problem and would be an "easy" fix. I know that a little slope or to much is bad, I have one spot in the main drain line that caused the problem. I can give dimensions, specs and hell I will take pictures for greater detail if anyone has an educated opinion if this is actually a good idea or not. He offered two repair prices, one for basically what I described and one for replacing everything. I think the pricing is ok it is more along the lines of the A/C is on the way out too and money is a tad tight.
 
Ya pictures would help.

Minimum slope on sewer lines is usually about 0.0050 (0.5%, or ~3/4" drop per 10' length), but that is risky. You want enough slope to keep small solids from settling. Minimum slope on septic systems here on this pipe is 2%, which is 1/4" per foot.
 
Pictures in the next day or so. Thanks for the help. This is not a septic system.


Oh, the problem is under the house in a crawlspace. I am thinking that the age of the pipe(house was built in 83) and maybe not enough support has slowly caused the pipe to sag? I will get under there with a level and check the slope when I take the pictures.
 
We generally try to get 1% (0.01 ft/ft) when going from a house to the main. Not sure too much fall is possible, I mean I wouldn't want 20% or anything, but I have have mains upwards of 7% on some projects.

As far as the fernco, yes you could cut the pipe and piece it back together. I am personally not a fan. Using a glue joint union would be my preference and make sure you support it because a fernco could pull apart if the lower pipe is just hanging in it.

Best advice I can give, don't pour grease down the sink. You may not, but if you do that is a super no-no. I'd say 90% of problems will trace back to grease + something else in the lines.
 
Thanks for the help. Spent some quality time under the house with my trusty sawzall and took out 3.5" and put a level on every piece of that pipe. All good now, went with just a little over 1/4" a foot.
 