The receptacle branch circuits are on 20A breakers, so a #12 wire is the correct size (assume the length is not too long). He only has 15A rated receptacle devices in the boxes, but that is acceptable per NEC (since he has more than one device in the circuit). If it was a single dedicated receptacle on a 20A circuit, then it would need to be a 20A rated device.
I would get a RELIABLE voltage meter, put it on the circuit and run the tool, watch what the voltage does. A clamp-style ammeter would also be helpful, if you can get one.
Thanks @KLF. I went with this guy due to budget restrictions right now. Think it will do the job? It's well-loved on Amazon, but not exactly a Fluke.
Amazon.com: Etekcity Auto Ranging Clamp Meter, Digital Multimeter with Amp,Volt,Ohm,Diode and Resistance Test: Automotive