flintknapper said:ANSWER:
The Pressure Temperature Relationship varies with ambient temperature.
Here is a guide line for R-134a (R-12 is slightly different).
Low Side..........High Side..........Ambient Temp. (F.)
16-29..............115-200..............70-80 deg.
19-39..............140-235..............80-90 deg.
25-43..............165-270..............90-100 deg.
37-51..............210-310..............100-110 deg.
As you can see ..."figures" rise as the ambient temp. rises.
In R134 systems the site glass is not an accurate means for determining that the refrigerant is correctly charged. That is what the manual is telling you. This is common knowledge. This is also why many manufacturers have eliminated site glasses from R134 systems.re_guderian said:...
pg AC-22. "Symptom - No bubbles present in sight glass. Amount of Refrigerant = None, suffcient, or too much" gee, that really helped...
..."*Bubbles in sight glass with ambient temperatures higher than usual can be considered normal if cooling is sufficient" ...
Rich said:In R134 systems the site glass is not an accurate means for determining that the refrigerant is correctly charged. That is what the manual is telling you. This is common knowledge. This is also why many manufacturers have eliminated site glasses from R134 systems.