I'd use 10 gauge 8/3 cord for...
Say what?
The longer the cord the more amp/volt drop/loss you will have. If you plan on having to use the welder that far away from the plug then I would up the AWG size personally.
The longer the cord the more amp/volt drop/loss you will have. If you plan on having to use the welder that far away from the plug then I would up the AWG size personally.
I would measure the input power at the receptacle to determine if the voltage loss is an issue. We have 245v coming out of our receptacle so voltage loss is a non issue for us.
Voltage Drop Calculator
I would measure the input power at the receptacle to determine if the voltage loss is an issue. We have 245v coming out of our receptacle so voltage loss is a non issue for us.
Voltage Drop Calculator
Figure this, an 8/3 cord at 100 feet will handle 60 amps all day long. 6/3 is overkill as one already ssaid, 10/3 is good for 50 ft but it will get warm.
I use a 75 ft 8/3 for my miller 252. I've never welded anything better than 3/8" with it. But it didnt get warm at all.
Sure, how far up was the dial turned? You probably wont have any problems medium duty when your only running maybe 20 or 30 amps. What about when your trying to burn some thick steel, or cut some steel and have it cranked all the way up? I think your gonna do that eventually.
The risk lies in full heat (amperage) and overheating the cord to the point where the insulation melts off it.
Though, you likely have it on a 40 amp breaker mr brokenparts where a 45 amp cable is protected. In which case the breaker will go before the cable is damaged.
If your running #8 (good for 45 amps) or worse yet #10 (good for 30 amps) on a 60 amp breaker, at full load you could burn the insulation off the cable and start a fire, or worse yet, you could burn off the jacket and have a bare conductor on a piece of ungrounded steel (think sheet of plate metal on wooden table or saw horses). Then your buddy or his buddies girlfriends cousins childs friends sister... leans against it with damp or sweaty arms or clothes.
And it might not be the welder thats the problem. Someone may use the cord for a kiln to heat ceramics or glass, or a range or oven for powder coating at a later date, and not even think about checking to see what size wire it, as long as the cord ends fit.
Point is, getting away with unsafe tools is one thing, recommending it to others is another. If you can spend $800-$2K on a decent welder, spend the extra $50-200 over the cost of cheap stuff, on a good welding cable as well.
the nec deals with building wiring. that is to say... permently installed in a building . extention cords and other plug in equipment i belive it's the "appliance manufactures assoc." ( i could be wrong since it's been many years since i last looked and it could be some other quasi governing group at this point) extention cords are used in "open air" an as such can handle greater loads than a wire concealed inside of a wall. that along with the welder's duty cycle , in effect limiting the load - 8/3 for me