alright...installed a 75k BTU garage heater, got the plumbing done this weekend...and no dice. I hate to call in someone that knows what they are doing, so here are the facts/symptoms...
100 gallon propane tank, 1/2" black pipe to unit. Tank is full, volume and pressure are (or should be) just fine - I "opened" up the connection orifice at the tank for flow.
Power to the unit is fine, as is the thermostat. It kicks on the exhaust fan, the valve control clicks, the heating element glows, then it kicks off...then the back fan fires, and it sequences thru the cycle 3 more times...
exactlee as the book states is should....I installed the conversion kit per instructions. Yes, the internal switch is set to on, and yes the green light operates as it should for the 4 cycles...then going to lockout mode wiht 6 blinks.
...and I have no heat.
Any thoughts on where to start? Knowing me, I missed something dumb, and hate to pay someone $100 to stop in and fix it with one tweak...
100 gallon propane tank, 1/2" black pipe to unit. Tank is full, volume and pressure are (or should be) just fine - I "opened" up the connection orifice at the tank for flow.
Power to the unit is fine, as is the thermostat. It kicks on the exhaust fan, the valve control clicks, the heating element glows, then it kicks off...then the back fan fires, and it sequences thru the cycle 3 more times...
exactlee as the book states is should....I installed the conversion kit per instructions. Yes, the internal switch is set to on, and yes the green light operates as it should for the 4 cycles...then going to lockout mode wiht 6 blinks.
...and I have no heat.
Any thoughts on where to start? Knowing me, I missed something dumb, and hate to pay someone $100 to stop in and fix it with one tweak...