LAMBCRUSHER
SILVER Star
you're better off(cheaper) to run your circuit to the first plug location and instal a gfi recep there. take the rest of that circuit(less freezer) from the out terminals on the GFI and install regular receps there after. the regular receps will be protected by the upstream GFI if wire off the out terminals of the gfi. It is a wash as far as the work goes and you don't save any wire one way or the other. a GFCI recep is like $15 whereas a breaker is like $50. the freezer CAN be part of the same circuit(tapped of the line BEFORE the GFI) but you should dedicate that IMO and use of a single recepticle makes lack of GFI protection at that location more acceptable(although after 09, EVERYTHING outside, in a garage, a commercial kitchen is supposed to be GFI protected by my interp of the code)