I am sure 2 Gauge is not nearly enough. You need 2/0 to maintain proper voltage and to carry the load 11 feet. I had conversations with both Xantex and Magnum about my install before buying the wire. I also used a 200 amp blade style fuse close to the battery. This is not just for inverter ovlerload but more so for inverter meltdown or in case the cable gets damaged, shorted, or somehow fails. You will have a serious problem if this happens and you are not fused. Get the fuse as close to the battery as possible.
found this:
Recommended Power and Ground Cable Sizes
which shows that to support 1000W, I need to use 2 guage cable
and this: American Wire Gauge table and AWG Electrical Current Load Limits with skin depth frequencies
which tells me that at 120A, which is the MAX power of the unit, there is about a 3.5% drop in a 11 foot wire, or .424 voltage drop. Which tells me that I should be fine as long as I don't expect the inverter unit to run at peak efficiency. I am willing to give up a bit for the unit to be setup cleanly where I want it. Interesting web pages.