x
A 100a panel just means that's what the panel itself is rated for, not what you can get out of it.
Don't dig up the 3". It's more than sufficient for anything you plan to do.
If your house panel has a main breaker, see what size it is, that governs your service size. You also have at least that much wire from it back to the pole. Typically more.
A 10kva is the smallest normal pole mount they use for homes. Good for about 40 amps at 240v. If you plan to have a shop, compressor, good sized welder and more activity there, a 25kva xfmr would be a good call, and is good for about 100amps at 240v. That would mean it's possible the wire you have is sufficient and wouldn't need to be changed. Check the size or the utility can tell you. But, you'd be surprised what you can do with 40a at 240v (80a at 120v), maybe you're just fine for a few years? They upgrading the xfmr for free?
The next size up is 50kva, and most likely you'd need new feeder wire, same conduit. I doubt you'd ever need this size xfmr.
Many variables, every utility is slightly different, but where I live they typically bring wire sized for 100a to every home as a minimum standard.
There's some disconnect here. You only need enough wire to match the rating of your main breaker, regardless of xfmr size. If they are suggesting a 25kVa xfmr, and you have a 100A MCB, then there is no need for a 200A feeder.
If you want a true 200A service, in that case yes, they would install a 50kVa xfmr and, to get the full capacity, you'd need to upgrade your house panel and main breaker to 200A.
Have they told you what wire is in the conduit now? How long is the run from the pole to the panel, and the panel to the future shop?
Feel free to PM me your number, or I'll give you mine.
Around here, when a home owner builds a home or upgrades service, the utility company pays/installs the feeders/drops to match upgraded panel.
200A upgrade is common here with the owner only paying for the new service panel install.
When I built my home back in 98, I installed a 400A panel that required the utility company to use much larger feeders. They weren't happy about having to return (delay) with larger wire but no charge was incurred on my part. I was responsible trenching and back filling the trench after inspection. They provided the shade (sand).
3" conduit is pretty big, I used 2" conduit for 200A feeders to the shop's sub panel. Seems they want an easy pull (who wouldn't) but check local code. If you don't need larger conduit per code, a simple call to the cooperation commission can get you results.
devil is in the details. total load, type of conductor and installation, and length of circuit are needed to finish the math. if the conduit is 3" that means it can house enough conductors of large enough capacity to feed your 320 amps. You should go for the larger pot(transformer), and max the wire in the conduit. 320 amps is alot of juice. the on line calc says you'll be just over 200 amps both legs at 50kva and by the math, 320 amps both legs full on would be
k(VA){1000 watts} = 320 amps x (actual voltage)240 / 1000
so 76,800 Volt-Amps(watts) / 1000(k) = 76.8 kVAs
Now that's alot of welding and air conditioning happening all at the same time.
Alot of the utilities consideration in saying you can get up to 320 amps might also be based upon your length of run. And that is going to be of a serious concern to you when you run from your service to your shop. Alot of guys don't give the voltage drops enough consideration of the types of loads you're talking about, so make sure your contractor mentions those very important factors and recommends upsizing considerably the wire to the shop. As long as you don't have to battle point of use voltage drop, 320 amps should be enough for a man (and :princess:) to be happy.
:worms:
For reference, Valley Hybrids service is rated at 100 amps 3 phase 208 volt or a total of 36.25 kVA, if that helps put things in perspective.
The shop is going to have:
  • car lift
Just FYI, the 10,000 lb. Dannmar D10/ACX lift I just installed requires a 25 amp, 220v circuit.
that's a big motor for a lift. good thing it only runs a few minutes at a time
I was always under the impression that the transformer was the utility's property, and you had to pay for the wires off of it to the house.
I have similar house shop setup to what you are talking about, we are 100% electric out here with no natural gas or propane for heat. We have a 400 amp 1 Ph service running to the house and pulled 200 off to feed the shop.
Some perspective on power requirements vs breaker size for some of the equipment you mentioned.
The Dannmar, Bendpack lifts require a 208-230 V / 30amp 60hz. 1 Ph service but they have a 2.5 HP motor that has an 11amp FL rating and mine only pulls 6amps when raising my 8000 lb Dodge truck.
My compressor is on a 208-230 V / 50amp 60hz service, it’s a 7.5 HP Gardner Denver Reward Series with a 23.1 CFM @ 175 PSI Rating, this compressor is large enough for a three man body shop running air tools and over kill for a single man shop. The motor has a 21amp FL rating and mine pulls about 15amps when running.
My full size mill and lathe both have very low amp draw when in use although they are both on a 30amp service.
My Miller Invision 450 is my largest welder and it’s on a 208-230 V / 100amp service, name plate says it will pull 49amps if I was welding @ 450 A at 36.5 VDC, 100% duty cycle, I don’t ever turn it up anywhere close to that and guess it’s only pulling 20amps or less when it’s turned up as high as I go.
My plasma cutter is on a 208-230 V / 50amp 60hz service, name plate says 50amps @ 100% duty cycle and I have popped the breaker a few times when cutting thick steel on the maximum settings.
In my one man shop with some fairly large power requirement equipment I don’t know that’s it’s possible to pull more than 100amps at any one time.
Obviously it’s your hard earned money and spend it how you see best but small to medium CNC mills still have 5/7.5 motors and don’t pull many amps when running under normal circumstances. A 200 amp panel should run everything on your current wish list and still have room to grow.
but I could see my dumb butt firing up the mill, plasma table, and then going out to fire up the welder ;)
The only possible way I could pull more than 100amps is turn multiple high Inrush current machines on during a power outage and let them all start at the exact time. Again not likely because most all my high amp draw machines have mag starters but you get the idea, you’ll need to try hard to overrun a 100amps in a single man shop if you use just limited common sense.
My house has three items that will be propane:
  1. HVAC (upper and lower floor, none in basement)
  2. Stove/cook top
  3. Tankless water heater
At least 100amps in my 200amp house panel is dedicated to these three electric items at my place.
Used to be that the power company would upgrade their systems based on your usage - upgrades meant that you’d use more/pay more and they wanted to facilitate that. With all the deregulation, most places have separated transmission from supply so upgrading services doesn’t directly affect income to the transmission company. It’s a cost to the transmission company and they don’t get any of the income from supplying you with more power - so they started charging for everything.
back when the power company was really subsidized...
100 amps to your shop will be fine. run it how they brung it; fill that pipe with wire and stick the biggest breaker they say OK to on the end of em.
you could just stick a 200 amp PV array and bank of prius batteies on your shed and call it a day...it's only money:hillbilly:$$$$$
My power co is a co-op. You aren't a customer you're a member. They are basically on a use it or lose it system as far as money goes. The system is a joy to work in because everything stays basically new, right of ways continually cleared, etc.
They are responsible up to the meter. When I had new power installed I was given the option of aerial or underground... Nothing extra for underground.
My understanding is you do have to pay for the additional transformers if you want 3-phase installed though.
Ok I just stumbled onto this thread. I looked at your pic, I looks like you have a 10 Kva transformer. The wire out of the transformer looks like 4/0 and goes down the pole. Does the wire going down the pole go strait to your house or does it hit a j-box and feed multiple homes.
If you are the only house on the transformer and and you have a 4/0 service or even a 1/0 service with in 150' of the pole you should be able to run a 200 amp service no problem. My advice is to get your panel upgraded and then complain to the power company if you are having power quality issues. I have seen up to 16 houses on a 50 kva transformer. Your 3" pipe is good for up to 350 mcm service wire which is enough to power a 400 amp service.
Is your electric service in 3" conduit all the way from the pole to the meter panel.