Thanks s lot!
Temps were 70-75. Typical socal morning.
My preference for sake of accuracy and ease of charging the system would be to wait until ambient temps reach 85° F.
Started with liquid in the low side. Which I think is NOT what the FSM calls for. Followed by liquid in tbe high side.
We will assume this was into vacuum (engine off)? You can liquid charge (into vacuum) from either side, but the high side is preferred. That way (high side) there is no danger of slugging the compressor with liquid refrigerant (which it can not compress). Any refrigerant introduced into the low side (as a liquid into vacuum) must first 'flash gas' before you start the compressor. Ideally....we don't want any (or very little) liquid refrigerant ever going into the low side while the compressor is running.
Is it possible that the low side is now "contaminated" with liquid when it needs to be vapor
Unlikely IF it has had time to 'flash' off and the ambient temp is sufficient. But don't liquid charge through the low side anymore.
and thus at ambient temp and not triggering the expansion valve to open because of the "high" temp?
The TXV bulb is filled with the same refrigerant (same for R12 or R134a) as you are using in your system, so it expands at the same rate (per temperature) which applies pressure against a diaphragm which moves the metering rod (a calibrated spring is used to control the travel and return the rod). The TXV seeks to control the superheat. Unless faulty (stuck open or closed, or sticky) it is not likely your issue.
The pressure switch is signaling so there is something in there and the compressor turns on but no flow.
Yes... your binary switch (combination low/high cut out switch) is working (at least the low side) or the compressor clutch would not be engaging. But we haven't yet determined that there is 'no flow' through the system. You've made an 'assumption' based solely on gauge pressures. There are some mechanical checks we need to perform. I think you are getting erroneous pressure readings on the low side because of hose/valve obstruction.
Wait that's all wrong I think
No, it's not ALL wrong. Most of it...but not 'all'. 
We don't want to lose any R12 already in the system if we can help it, so let us know when you have time to get back on the project and we can go from there.