I'm still having a problem with my compressor not cycling. I've already fried two compressors because they weren't cycling before I realized the problem. Bought gauges and see that the pressure on the high side keeps rising to the point that it damages the compressor. Replaced the pressure switch but that makes no difference. Gauges showing 50 low side and 400 high side before I turn A/C off. Any ideas why the pressure switch won't cycle off the compressor?

Sorry for the lengthy post. Hope it makes sense.
 
Is the pressure switch new? If the switch and wiring are working properly, the compressor will shut down when too low or too high of a pressure occurs that could damage your compressor. If the pressure switch wiring harness is unplugged the compressor should not turn on unless a PO bypassed the wiring going to the switch. I would test the wiring by unplugging the wiring harness to the switch. If that test works, I would suspect a faulty pressure switch. As far as the higher pressures, was the system overcharged?
 
Is the pressure switch new? If the switch and wiring are working properly, the compressor will shut down when too low or too high of a pressure occurs that could damage your compressor. If the pressure switch wiring harness is unplugged the compressor should not turn on unless a PO bypassed the wiring going to the switch. I would test the wiring by unplugging the wiring harness to the switch. If that test works, I would suspect a faulty pressure switch. As far as the higher pressures, was the system overcharged?


Pressure switch is working as far as I can tell. If I unplug it the compressor cycles off. Compressor won't engage until the minimum amount of freon is added, which is what it should do. I'm pretty sure I didn't add too much freon. The sticker says 1.9lbs max.
 
The pressure switch is on the other side of the condenser. If the condenser is not working propery (clogged) would that cause my problem (high pressures on high pressure side)
 
Send a PM to 1972FJ55 (Rex) and ask him to look at this thread.

He is an A/C guru and very nice guy.
 
The system is way overcharged. The only time you should be seeing pressures that high is at ambient temps above 130 ish.
 
I'd suspect an overcharge, a weak/bad fan clutch, or a restriction in the system (a plugged condenser?). Why did you replace the compressor originally? New drier?

Douglas, 1972FJ55 is the guy that can help you solve your AC problem. Give him as much info as you can.

John
 
Some more information

I changed out the compressor, drier, evaporator, and expansion valve. I put a vacuum on the system and checked for leaks using manifold gauges. I added 30 oz of freon. The low side gauge reads 50 psi with compressor engaged. The high side is the problem. I'm getting high side gauge readings around 400 psi because the compressor won't cycle off. Am getting good cold air from the A/C. The problem I think is the compressor won't disengage because perhaps the condensor is partially clogged which affects the ability of the pressure on the pressure switch side to rise enough to disengage the compressor?
 
Just went thru the a/c on my son's rig this week myself. I typically charge to upper 30's then bleed down to low 30's on the low side after it stabilizes no matter what brand of vehicle I'm working on in the garage (80'ish degrees in the shade). You'll find charts on-line saying higher but I've found 50psi is significantly high which will can cause excessive strain on the system and higher values on the high side as well and won't cool as well. My recommendation is to bleed the system down to an appropriate low side pressure. I usually see values as high as yours from folks that buy an add-a-can system hoping it was just low when they attempt to fix their a/c, pretty common. High side should read close to 2(outside temp)+50 give or take a bit. Expansion valves can cause the high to be off the charts as well but make sure you're comfortable with what you're low is reading before concluding that is the problem. A/C is finicky and there are plenty of opinions on how it should be set-up. I can only report better personal success keeping the low on the lower side of the limits.
 
Last edited:
did you replace the expansion valve before all this went to hell? therefore, are you sure the expnsion valve is properly installed?
 
Aside from a possible problem with the high pressure cut-out switch/wiring, I would say you have way over charged the system with refrigerant. Do you know how much refrigerant was added the previous two times by weight? If there was a blockage, I'd suspect that your suction pressure would be much lower than 50 psi.
 
Sh$t missed that. Better put away the rum. For a discharge pressure that high, something is really wrong. It's been s long time since I worked developing HVAC systems, but still seems like an overcharge situation.

The Symptoms Of Refrigerant Overcharge
 
As mentioned by many- 50 is too high, period! Bleed it off until you are running around 35 on the low side. Or, bleed until you see bubbles in the sight glass, which is the best, un-scientific way to charge the unit, other than weighing it in. If your system does not run correctly with about 35 on low side, then you have another problem.
 