this seems to be the right place to ask this question since it is very close to vtcruiser's. If I have a two pole 40 amp dual pole breaker on my house box that covers the cable running to the garage, and there is a small breaker box in the garage with three 15 amp breakers, one for lights and two for different sets of wall plugs, is there any reason why I can't add a two pole 20 amp breaker to the small box so I have a 220 amp citcuit out there? I can't actually see the wire since it is in conduit but whatever it is should handle 20 amps shouldn't it? I just bought a 3000 watt 230 v blower/heater for the garage and I was thinking I'd need to run a separate cable but now I'm thinking that the heater is only going to draw 13 amps at 220v so i should be good?
and while we are there, the box in the garage has no groundwire, but the cable to the house is in metal conduit. Is that an acceptable ground? It was built in 1998 and it sure looks like this thing was built to code.