I last summer I completely overhauled my AC system. New compressor, new condenser, new expansion, TXV valve new evaporator, flushed the lines.

AC was working great after all that.

Fast forward. The AC system is not working like last season.
When starting up the AC system it did not blow cold at all. In fact the compressor was not turning /engaging. Even when the console indicated that the AC, compressor was on, with max cold, and setting set on HI this system. Sure enough, the compressor was not turning at all.

I checked to see if there was Freon in the system through the Schrader valve and there was.

Then I tried filling the system with freon and nothing was coming out. and the AC compressor was still not working. After shaking again, and re-attaching, the system I was elated to see the AC compressor kick in.

The Freon bottle was starting to feel cold, but only for a few seconds. The gauge moved from zero/LOW to about 35 psi . Then gauge went back to zero. And the Freon stopped delivering.

So even shaking the Can and Doing the 12/6 o’clock thing the system simply stopped accepting additional Freon. I don’t think very much came out at all. However, the AC compressor was still running.

Any ideas ?
 
Did you use refrigerant that comes in cans that anyone can buy? Usually those aerosol can style r134 have crap hoses
I hear you. I have 134a cans that you have to pierce. I think they stopped selling those but I still have a few left over.

As for the hose gauge I have one from inter dynamics that ls probably 6 years old now.

I have modern adapter for the newer can tops so I’ll try that.

If that’s what the issue is I will be thrilled after replacing everything last season(!).
IMG_6216.webp
 
I do residential HVAC, AC cycle is similar to cars

From what I understand, the pressure switch can leave the compressor circuit open rather its low pressure or high pressure. I would get a set gauges that has low, high, and charge hoses. Then you can check both sides of the ac cycle.

Cars usually weigh in the refrigerant charge, instead of charging by pressure

Additionally, if you changed all those parts yourself, there are a few more steps to take.

First, I would purge the ac lines with nitrogen.

Second, you are suppose to pressure test with nitrogen. It gets rid of some moisture and to check for leaks.

Third, before charging refrigerant is to run a vacuum, it pulls out everything in the system, contaminants and non-condensables. The ac system suppose to be only refrigerant /oil inside.

When everything checks out, then charge system.
 
Last edited:
Hi thanks for your insight. Yes, I did everything you had mentioned other than filling with nitrogen. I believe I’ve use some sort of alcohol-based flushing agent. And then I vacuumed down the system for awhile and it held pressure for a good length of time. Added the FSM amount of PAG to the compressor and condenser too.

I do have a set of manifold gauges to deliver the Freon as well. Good that you remind me that I should consider that option too.

I believe you alluded to the amount of Freon that needs to be in the system for the compressor to even kick on. This has happened before where there was not enough Freon in the system and the compressor would refuse to engage and frustrate my goal of adding Freon to the system. Here, the compressor finally kicked on (still does), so now I hope to use the manifold gauges to deliver it.

hoping the manifold set will work.

Otherwise I’ll consider your tip of evacuating all the Freon in the system, captured by a professional, and then nitrogen/vacuum lines again before filling back.
 