    I'm renovating a 1978 house that currently has 100 amp service. I'm not sure what size wire is going from the transformer to my house. But the 3" conduit will support up to 320 amp wiring/service. In order to get bigger service, I will have to dig up/replace the 3" conduit.

    The house is 1900 square feet plus about 400 square foot of basement/temp shop.

    I will be getting a large shop in the future. It will get a lift and hopefully before I die I can find a reasonable price mill or lathe :)

    I'm being told the current transformer is 10kva and it is being recommended I go to 25kva.:eek:

    I will double check but I believe I'm the only one on the transformer... mountain house:hillbilly:

    So the basic question I have is: Is my electric company trying to pull a fast one on me?
     
    1911 likes this.
  2. mdsims

    mdsims

    Messages:
    614
    Likes Received:
    268
    Joined:
    Jun 11, 2013
    Location:
    San Jose, CA
    A 100a panel just means that's what the panel itself is rated for, not what you can get out of it.

    Don't dig up the 3". It's more than sufficient for anything you plan to do.

    If your house panel has a main breaker, see what size it is, that governs your service size. You also have at least that much wire from it back to the pole. Typically more.

    A 10kva is the smallest normal pole mount they use for homes. Good for about 40 amps at 240v. If you plan to have a shop, compressor, good sized welder and more activity there, a 25kva xfmr would be a good call, and is good for about 100amps at 240v. That would mean it's possible the wire you have is sufficient and wouldn't need to be changed. Check the size or the utility can tell you. But, you'd be surprised what you can do with 40a at 240v (80a at 120v), maybe you're just fine for a few years? They upgrading the xfmr for free?

    The next size up is 50kva, and most likely you'd need new feeder wire, same conduit. I doubt you'd ever need this size xfmr.

    Many variables, every utility is slightly different, but where I live they typically bring wire sized for 100a to every home as a minimum standard.
     
    Last edited: Mar 17, 2017
    jeffro109 likes this.
  3. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    I understand most of that.

    Shop is going to start with standard 220V welder and air compressor. I will be stuffing a lift, plasma cutter, and mill as funds allow. So yes, a bit of a draw:censor:

    From what I was told, the current wire in the conduit will not get me to 200 amp. So I need new wire.

    I was told the 3" could be sufficient for 320amp wiring. There is no way to get 400amp or more.

    I was told due to the size of the parcel, there is no way for me to get a separate pull to the shop.

    Free? This is PG&E, they are going to bend me over badly and probably use a cactus... the new estimator has already doubled the old estimator's guestimate.:eek:
     
  4. mdsims

    mdsims

    Messages:
    614
    Likes Received:
    268
    Joined:
    Jun 11, 2013
    Location:
    San Jose, CA
    There's some disconnect here. You only need enough wire to match the rating of your main breaker, regardless of xfmr size. If they are suggesting a 25kVa xfmr, and you have a 100A MCB, then there is no need for a 200A feeder.

    If you want a true 200A service, in that case yes, they would install a 50kVa xfmr and, to get the full capacity, you'd need to upgrade your house panel and main breaker to 200A.

    Have they told you what wire is in the conduit now? How long is the run from the pole to the panel, and the panel to the future shop?

    Feel free to PM me your number, or I'll give you mine.
     
    Lil'John likes this.
  5. firestopper

    firestopper

    Messages:
    632
    Media:
    125
    Albums:
    2
    Likes Received:
    355
    Joined:
    Apr 15, 2012
    Location:
    Tucson, Az
    Around here, when a home owner builds a home or upgrades service, the utility company pays/installs the feeders/drops to match upgraded panel.
    200A upgrade is common here with the owner only paying for the new service panel install.

    When I built my home back in 98, I installed a 400A panel that required the utility company to use much larger feeders. They weren't happy about having to return (delay) with larger wire but no charge was incurred on my part. I was responsible trenching and back filling the trench after inspection. They provided the shade (sand).
    3" conduit is pretty big, I used 2" conduit for 200A feeders to the shop's sub panel. Seems they want an easy pull (who wouldn't) but check local code. If you don't need larger conduit per code, a simple call to the cooperation commission can get you results.
     
    thatcabledude and Lil'John like this.
  6. LAMBCRUSHER

    LAMBCRUSHER

    Messages:
    10,097
    Likes Received:
    2,654
    Joined:
    Aug 26, 2009
    Location:
    F'lost
    devil is in the details. total load, type of conductor and installation, and length of circuit are needed to finish the math. if the conduit is 3" that means it can house enough conductors of large enough capacity to feed your 320 amps. You should go for the larger pot(transformer), and max the wire in the conduit. 320 amps is alot of juice. the on line calc says you'll be just over 200 amps both legs at 50kva and by the math, 320 amps both legs full on would be
    k(VA){1000 watts} = 320 amps x (actual voltage)240 / 1000
    so 76,800 Volt-Amps(watts) / 1000(k) = 76.8 kVAs
    Now that's alot of welding and air conditioning happening all at the same time.
    Alot of the utilities consideration in saying you can get up to 320 amps might also be based upon your length of run. And that is going to be of a serious concern to you when you run from your service to your shop. Alot of guys don't give the voltage drops enough consideration of the types of loads you're talking about, so make sure your contractor mentions those very important factors and recommends upsizing considerably the wire to the shop. As long as you don't have to battle point of use voltage drop, 320 amps should be enough for a man (and :princess:) to be happy.
    :worms:
     
    LandCruiserPhil and Lil'John like this.
  7. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    mdsims, thank you for the offer for the call. I don't want to waste your time too much with a basic fact checking post :)

    The first guy I talked with back in September gave me a "usually this costs $x" This new guy has doubled it so I'm a bit confused.

    Here is the lot picture:
    shop_2.jpg

    For some specifics:
    Transformer to side of house is under 150 feet. The transformer is at the bottom of the picture below the 06254. The meter is on the north east corner of the house. My under 150 feet guestimate is from the house being 44' long and I used ~80 foot of conduit to pull fiber optic from same pole to the south east of the house ;)
    From NE side of the house to the shop will be about 100 feet... the location is very much in flux... but imagine from the green box or the horse corral below it.

    The house is going to have:
    • Two HVAC systems (upper floor/lower floor, gas heat)
    • Hot tub
    • Fridge and separate freezer
    • Dishwasher/trash compactor
    • Office/network closet (running two 20 amp circuits for network closet)
    • Gas stove
    • Electric clothes washer/drier
    • 50amp 220 run for welder in basement, won't be used once shop is up
    • Unknown well pump and pressure tank
    • Usual mix of indoor/outdoor lighting/electrical for 1900 square foot house
    The shop is going to have:
    • 50 amp 220 run for welder/plasma cutter
    • 50 amp 220 run for air compressor (don't have)
    • Mill, hopefully CNC (eventual)
    • car lift
    • Lots of grinders and power tools :p
    Shop is mostly going to be one man use. Size is lightly in flux: 50x50 will fit corral area, 30x70 is green box ;)
     
    Last edited: Mar 19, 2017
    1911 likes this.
  8. LAMBCRUSHER

    LAMBCRUSHER

    Messages:
    10,097
    Likes Received:
    2,654
    Joined:
    Aug 26, 2009
    Location:
    F'lost
    For reference, Valley Hybrids service is rated at 100 amps 3 phase 208 volt or a total of 36.25 kVA, if that helps put things in perspective.
     
  9. thatcabledude

    thatcabledude SILVER Star

    Messages:
    2,210
    Likes Received:
    2,002
    Joined:
    Oct 20, 2011
    Location:
    DeFuniak Springs, FL
    Where I'm at that would get its own meter if you wanted it.
     
  10. 1911

    1911 chupacabra SILVER Star

    Messages:
    4,408
    Likes Received:
    1,674
    Joined:
    Aug 11, 2006
    Location:
    Parker County, Texas
    Just FYI, the 10,000 lb. Dannmar D10/ACX lift I just installed requires a 25 amp, 220v circuit.
     
  11. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    Sadly, they wouldn't do anything for me due to "small" lot size(five acre)

    That is the rating I was expecting on a lift. Fortunately, most of the items would only be used one at a time. The exception would be compressor and plasma cutter ;)
     
    1911 likes this.
  12. LAMBCRUSHER

    LAMBCRUSHER

    Messages:
    10,097
    Likes Received:
    2,654
    Joined:
    Aug 26, 2009
    Location:
    F'lost
    that's a big motor for a lift. good thing it only runs a few minutes at a time
     
  13. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    Thank you again for the input.

    Is it possible to identify a transformer's size based upon external characteristics?

    Here is what is feeding my house:
    0404171644.jpg
    Yes, I'm the only house on it.
     
  14. jeffro109

    jeffro109

    Messages:
    1,336
    Likes Received:
    324
    Joined:
    Sep 12, 2010
    Location:
    North East TN
    I was always under the impression that the transformer was the utility's property, and you had to pay for the wires off of it to the house.
     
    Lil'John likes this.
  15. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    I was mostly expecting this.

    But the transformer is on me... they are calling out the lines under the gray plastic cover on the pole as a "riser" and they are on me.
     
  16. J Mack

    J Mack

    Messages:
    1,708
    Likes Received:
    1,301
    Joined:
    Sep 17, 2013
    Location:
    Boise Idaho
    I have similar house shop setup to what you are talking about, we are 100% electric out here with no natural gas or propane for heat. We have a 400 amp 1 Ph service running to the house and pulled 200 off to feed the shop.

    Some perspective on power requirements vs breaker size for some of the equipment you mentioned.

    The Dannmar, Bendpack lifts require a 208-230 V / 30amp 60hz. 1 Ph service but they have a 2.5 HP motor that has an 11amp FL rating and mine only pulls 6amps when raising my 8000 lb Dodge truck.

    My compressor is on a 208-230 V / 50amp 60hz service, it’s a 7.5 HP Gardner Denver Reward Series with a 23.1 CFM @ 175 PSI Rating, this compressor is large enough for a three man body shop running air tools and over kill for a single man shop. The motor has a 21amp FL rating and mine pulls about 15amps when running.

    My full size mill and lathe both have very low amp draw when in use although they are both on a 30amp service.

    My Miller Invision 450 is my largest welder and it’s on a 208-230 V / 100amp service, name plate says it will pull 49amps if I was welding @ 450 A at 36.5 VDC, 100% duty cycle, I don’t ever turn it up anywhere close to that and guess it’s only pulling 20amps or less when it’s turned up as high as I go.

    My plasma cutter is on a 208-230 V / 50amp 60hz service, name plate says 50amps @ 100% duty cycle and I have popped the breaker a few times when cutting thick steel on the maximum settings.

    In my one man shop with some fairly large power requirement equipment I don’t know that’s it’s possible to pull more than 100amps at any one time.
     
    LAMBCRUSHER and Lil'John like this.
  17. Lil'John

    Lil'John SILVER Star

    Messages:
    4,491
    Likes Received:
    454
    Joined:
    Mar 24, 2006
    Location:
    Nor Cal in the garage with a Cruiser
    Thank you for the input there J Mack.

    My house has three items that will be propane:
    1. HVAC (upper and lower floor, none in basement)
    2. Stove/cook top
    3. Tankless water heater
    For the most part, my shop will be just me with as much "automation" as I can squeeze in:
    1. CNC mill
    2. CNC plasma cutter
    The automation part is mainly for accuracy/duplicatability... but I could see my dumb butt firing up the mill, plasma table, and then going out to fire up the welder ;)
     
  18. J Mack

    J Mack

    Messages:
    1,708
    Likes Received:
    1,301
    Joined:
    Sep 17, 2013
    Location:
    Boise Idaho
    Obviously it’s your hard earned money and spend it how you see best but small to medium CNC mills still have 5/7.5 motors and don’t pull many amps when running under normal circumstances. A 200 amp panel should run everything on your current wish list and still have room to grow.
    The only possible way I could pull more than 100amps is turn multiple high Inrush current machines on during a power outage and let them all start at the exact time. Again not likely because most all my high amp draw machines have mag starters but you get the idea, you’ll need to try hard to overrun a 100amps in a single man shop if you use just limited common sense.
     
  19. J Mack

    J Mack

    Messages:
    1,708
    Likes Received:
    1,301
    Joined:
    Sep 17, 2013
    Location:
    Boise Idaho
    At least 100amps in my 200amp house panel is dedicated to these three electric items at my place.
     
    Lil'John likes this.
  20. PAToyota

    PAToyota Keystone Cruisers SILVER Star

    Messages:
    1,140
    Likes Received:
    116
    Joined:
    Oct 4, 2009
    Location:
    South Central Pennsylvania
    Used to be that the power company would upgrade their systems based on your usage - upgrades meant that you’d use more/pay more and they wanted to facilitate that. With all the deregulation, most places have separated transmission from supply so upgrading services doesn’t directly affect income to the transmission company. It’s a cost to the transmission company and they don’t get any of the income from supplying you with more power - so they started charging for everything.
     
    Lil'John likes this.