just moved into an old house (1940's) that has been renovated. PO installed a new electrical box but when i opened it i found nothing labeled. no biggie, so i turned everything on and started flipping breakers. found that the kitchen, living room & dining room all wired to a 15A breaker so, basically i can't run the dishwasher, microwave or lights in the house at the same time. what's my best option here? should i just run a separate line for the dw and be done with it?


__________________
Running total of non-waving FJC drivers ......534

'85 FJ60 bone stock (the way i like it)

'87 Ford Ocnorb with lots of redneck stuff & custom dented body panels
sk8salomon is offline   Reply With Quote
Old 12-16-07, 12:27 PM   #2
In the garage
 
John Smith's Avatar
 
Join Date: Jun 2004
Location: Maryland
TLCA# 9074
Posts: 1,707
Sounds like you need to run a few new dedicated circuits to the kitchen. Hopefully the new panel has some open space.


__________________
79 FJ40 & 78 FJ55
http://users.starpower.net/johnsmith <- Detailed ToyBox install instructions
Please help save the Upper Tellico OHV area, Donate to the Rescue Tellico Fund http://www.sfwda.org/trails/tellico/donate.html
John Smith is online now   Reply With Quote
Old 12-16-07, 01:53 PM   #3
IH8MUD Addict
 
FJ40_owner's Avatar
 
Join Date: Aug 2005
Location: El Dorado County CA
TLCA# 16294
Posts: 546
Quote:
Originally Posted by sk8salomon View Post
just moved into an old house (1940's) that has been renovated. PO installed a new electrical box but when i opened it i found nothing labeled. no biggie, so i turned everything on and started flipping breakers. found that the kitchen, living room & dining room all wired to a 15A breaker so, basically i can't run the dishwasher, microwave or lights in the house at the same time. what's my best option here? should i just run a separate line for the dw and be done with it?
Dishwasher, garbage, MW and refrig on a circuit.

Additional circuit for wall sockets. In the perfect world I would have two 15 Amp ciscuits for plugs to allow simutaneous use of e frying, toasting, blending, etc.

Remove the power, be safe.

JB


__________________
Third generation Californian! If you don't like it here, leave. And take your fat wife and screeming kids with you.
FJ40_owner is offline   Reply With Quote
Old 12-16-07, 02:20 PM   #4
IH8MUD Lifer
 
LandCruiserPhil's Avatar
 
Join Date: Mar 2004
Location: in a bus
Posts: 2,788
Run 2 new 20A (12/2 romex) dedicated circuits. 1 for dishwasher and 1 for the micro.
If you are low on breaker space in most cases you can use 1/2 size breakers if needed.

Not an uncommon problem for a house built in the 40s..didnt have dishwasher and micro back then.


__________________
"Knowledge without experience is just information"
Copper State Cruisers #003
LandCruiserPhil is online now   Reply With Quote
Old 12-16-07, 03:23 PM   #5
IH8MUD Junior
 
tehcruiser's Avatar
 
Join Date: Oct 2007
Location: nw
Posts: 151
A kitchen should not have any 15Amp. circuits, except for lights.
But things being what they are, you should definitely run another 15A for the dishwasher, which is the recomended minimum. The microwave is another power hog, and should have it's own dedicated circuit, but a 20A circuit will handle both just fine. You should also have at list two more circuits for the counter-top loads, and a dedicated one for the fridge.


__________________


Move along folks, nothing to see here!
tehcruiser is offline   Reply With Quote
Old 12-16-07, 06:04 PM   #6
IH8MUD Addict
 
sk8salomon's Avatar
 
Join Date: Apr 2006
Location: Chattanooga, TN
Posts: 706
ok thanks guys. the more i think about it, the more i want to boot the PO in the nuts. the family room is on the circuit which has the tv, stereo and lights. the dining room has a chandellier with dimmer switch and outlets near the floor on this circuit as well...then the kitchen. so basically the entire center of the house is run on this one 15A breaker
IDIOT IMO!


__________________
Running total of non-waving FJC drivers ......534

'85 FJ60 bone stock (the way i like it)

'87 Ford Ocnorb with lots of redneck stuff & custom dented body panels
sk8salomon is offline   Reply With Quote
Old 12-16-07, 06:08 PM   #7
IH8MUD Lifer
 
LandCruiserPhil's Avatar
 
Join Date: Mar 2004
Location: in a bus
Posts: 2,788
Quote:
Originally Posted by tehcruiser View Post
A kitchen should not have any 15Amp. circuits, except for lights.
But things being what they are, you should definitely run another 15A for the dishwasher, which is the recomended minimum. The microwave is another power hog, and should have it's own dedicated circuit, but a 20A circuit will handle both just fine. You should also have at list two more circuits for the counter-top loads, and a dedicated one for the fridge.
Min circuit of 20A for dishwasher per NEC code.


__________________
"Knowledge without experience is just information"
Copper State Cruisers #003
LandCruiserPhil is online now   Reply With Quote
Old 12-16-07, 06:15 PM   #8
Causin' a Ruckuss
 
UNBREAKABLE's Avatar
 
Join Date: Apr 2006
Location: Lenoir, NC
TLCA# 16090
Posts: 350
It would prob. be in your best intrest to rewire your house

Pull the panel cover and snap a pic...let's see what your workin with

edit: you are supposed to have 2 GFCI circuits in the kitchen....but being an old house your prob. not gonna get that


__________________
UNBREAKABLE FAB---Our rigs look better on their back than your girl does!
I'm a MARLIN CRAWLER DEALER...PM ME!
UNBREAKABLE is offline   Reply With Quote
Old 12-16-07, 06:29 PM   #9
IH8MUD Addict
 
sk8salomon's Avatar
 
Join Date: Apr 2006
Location: Chattanooga, TN
Posts: 706
no GFI in kitchen, only in bathrooms. at first glance, all the outlets in the house are new with the grounding plug. but when you test across the ground, it still has the old wiring so no true earth ground. THEY TRICKED US!!!!!!!!!


__________________
Running total of non-waving FJC drivers ......534

'85 FJ60 bone stock (the way i like it)

'87 Ford Ocnorb with lots of redneck stuff & custom dented body panels
sk8salomon is offline   Reply With Quote
Old 12-16-07, 07:16 PM   #10
IH8MUD Lifer
 
LandCruiserPhil's Avatar
 
Join Date: Mar 2004
Location: in a bus
Posts: 2,788
Grounded outlets are approved on a non-grounded system if the circuit has GFI protection. Almost all houses wired in romex prior to 1968 are non grounded system.


__________________
"Knowledge without experience is just information"
Copper State Cruisers #003
LandCruiserPhil is online now   Reply With Quote
Old 12-16-07, 10:35 PM   #11
IH8MUD Junior
 
tehcruiser's Avatar
 
Join Date: Oct 2007
Location: nw
Posts: 151
Quote:
Originally Posted by LandCruiserPhil View Post
Min circuit of 20A for dishwasher per NEC code.
I personally don't like anything under 20A, but I've come to the conclusion that sometimes you got to work with what you have. (Money, Time, Materials)


__________________


Move along folks, nothing to see here!
tehcruiser is offline   Reply With Quote
Old 12-17-07, 11:21 AM   #12
IH8MUD Lifer
 
fj40charles's Avatar
 
Join Date: Dec 2002
Location: Texas
Posts: 1,119
Also, if you're going to run new circuits, use 12 gauge for everything. Don't bother buying 14 gauge wiring.


__________________
69 FJ40 with some minor mods...
2000 Cummins powered Dodge with some power enhancements.

DO NOT SUPPORT TRAIL GEAR!!!!! bad ethics = bad business!

http://www.paypalsucks.com
fj40charles is online now   Reply With Quote
Old 12-18-07, 12:35 PM   #13
IH8MUD Lifer
 
stayalert's Avatar
 
Join Date: Sep 2004
Location: Norwich, VT
Posts: 1,001
pffft at least you have cicuit breakers!!!

My last house had screw in glass fuses......60 amps for a 5 bedroom house - 60 amps wasn't trouble some but the knob and tube wiring was 60 amps wasn't an issue 'cause there was gas hot water gas boiler and gas stove/oven & dryer.

first thing we did when we bought that house was gut it. we lived in a tent in the back yard for the summer and had demolition parties every night after work. Fun times....

Good luck and don't get zapped!!
stayalert is offline   Reply With Quote
Old 01-22-08, 12:27 PM   #14
IH8MUD DAD
 
VanGo's Avatar
 
Join Date: Oct 2007
Location: Bolling AFB, DC
TLCA# 18273
Posts: 73
I agree with unbreakable. Unfortunately cost is going to be a big issue, but it beats becoming homeless because you did not take preventive measures. Install 20A half breakers, if room is an issue. Or, at best, you might be able to install a 100A sub-panel, clean things up at the main. Then make your dedicated circuits for lights, receptcals, dishwasher, dryer, kitchen/bath, spare room, etc... Dedicated2- 20A breakers (12/2 romex) is a min. /NEC. Consult with a qualified electrician. Also, check out Tauton press fine homebuilding electrical great resource.

Van


__________________
Van
97 FJZ80, 40th, Locked, 285/75/16
67 M416
05 Excursion
VanGo is offline   Reply With Quote
Old 01-22-08, 01:21 PM   #15
IH8MUD Regular
 
Plowboy's Avatar
 
Join Date: Apr 2002
Location: On a hill overlooking a lake in Idaho
Posts: 429
Quote:
Originally Posted by LandCruiserPhil View Post
Grounded outlets are approved on a non-grounded system if the circuit has GFI protection. Almost all houses wired in romex prior to 1968 are non grounded system.
I have found in a lot of remodel that I have done in older home using the old cloth covered romex that the boxes have been grounded with the ground wrapped around one of the nails used to attach the box to the studs


__________________
78LC40, sbc 327, PuPs, Aussie Locker, 4wdisc. 1948 bradley trailer
Plowboy is offline   Reply With Quote
Old 01-22-08, 05:46 PM   #16
IH8MUD Lifer
 
LandCruiserPhil's Avatar
 
Join Date: Mar 2004
Location: in a bus
Posts: 2,788
Quote:
Originally Posted by Plowboy View Post
I have found in a lot of remodel that I have done in older home using the old cloth covered romex that the boxes have been grounded with the ground wrapped around one of the nails used to attach the box to the studs
I have found similar wiring also. When grounded romex was first available they didnt know what the ground because they did not have 3 prong outlets yet. Out west you will find the ground wires stuck out the back of the box and crimped. Remember 3 prong adapters, you needed to screw the adapter to plate screw so you could pick up your ground threw the yoke of the outlet.


__________________
"Knowledge without experience is just information"
Copper State Cruisers #003
LandCruiserPhil is online now   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On
Forum Jump


All times are GMT -6. The time now is 03:10 PM.


vBulletin® v3.7.3 ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0
©2000-2008 by IH8MUD™ - ALL RIGHTS RESERVED

Thanks to all those who have contributed!
One of the largest message boards on the web !




Infrared Sauna | Jewish Israel | Remortgaging | Credit Cards | Babb Fest