You don't have to backfeed at the meter, at least not in PG&E territory (SCE, LADWP, SDG&E, Oregon and Arizona... pretty much everywhere else, you do... or at least you need a safety switch at the meter)
There's a section of NEC 690 called the 120% backfeed rule... basically you can backfeed up to 120% of the main panel rating... so, if you have a 200A system, you can back-feed 40A safely onto the busbars. Now, the largest PV system that you can fit onto 40A (you kids with the calculators hang on, it's more complicated then straight ole math), is a 9.6kW DC (aka "Rated" or "PTC") system. General "rule of thumb", is that a 1kW DC system, will produce 1500kWH AC annually. So, that 9.6kW system that you can fit on your 200A panel, will spit out about 14,400 kWH.
If you want anything larger, we'd have to connect via a line-side tap, which circumvents the panel all together and generally means tying into the meter (or at least near it).
|