01-11-07, 02:26 PM
|
#1 (permalink)
| | Forum Regular
Join Date: Oct 2004
Posts: 216
| Shop question about 220v outlets I have a 30 amp 110/220 outlet for a dryer in my basement. Can I plug 220v tools--like table saws and air compressors--into that (provided I make an adapter cord so it can fit the outlet)? Or do I need a dedicated 220v outlet?
Timoss
88 fj62 TLCA
Last edited by Timoss; 01-11-07 at 02:34 PM.
|
| |
01-11-07, 02:29 PM
|
#2 (permalink)
| | 250+ Club
Join Date: Jan 2005 Location: Tulsa, OK
Posts: 476
| You can if the tools is rated less than 30 amps and the dryer is not running at the same time.
__________________ Dave Stinchcomb
Green Country Cruisers
1981 FJ60
1976 FJ40
1966 FJ40 |
| |
01-11-07, 03:05 PM
|
#3 (permalink)
| | Forum Regular
Join Date: Oct 2004
Posts: 216
| So the fact that the dryer outlet is dual voltage 110/220 does not matter? I know very little about these things...
Timoss
88 fj62 TLCA |
| |
01-11-07, 03:37 PM
|
#4 (permalink)
| | Forum Lifer
Join Date: Mar 2004 Location: Scottsdale Arizona
Posts: 3,964
| 220V is just 2 - 110V line 180* out of phase.
So the answer to your question is no.
__________________ "Knowledge without experience is just information"--Mark Twain Copper State Cruisers #003 |
| |
01-11-07, 04:16 PM
|
#5 (permalink)
| | Forum Lifer
Join Date: Jan 2005 Location: Reno
Posts: 6,231
| Quote:
Originally Posted by Timoss So the fact that the dryer outlet is dual voltage 110/220 does not matter? I know very little about these things...
Timoss
88 fj62 TLCA |
Your dryer, based upon your description, can operate on either 110V or 220V...however the wiring needs to be changed within the dryer depending whether you are feeding it 110V or 220V (check the owner's manual and/or the rear inside/outside panel of the dryer for instructions).
Your 220V outlet, I think by code, has to be dedicated and not shared. You can run any appliance/tool that you want as long as it is designed/rated for 220V/30A power. If your device needs 220V/50A power then they are not compatible.
__________________ Modded '99 for overlanding/exploring: 35's, 4.88's, AO drawers, Slee rr, TJM fr, ARB fr locker, ear candy, Waeco CF-50, PowerGate with 2nd battery with custom home brew battery tray, home brew sliders & Slee belly and skid plates, 9.5XP/Masterpull, Solstice LEDs, OEM 864's, Foxes x 4, 12mm BL, Carl's UCAs, LT285/75R18 GY MT/R Kevlar, KK in tow... HAMified
ROTM: http://forum.ih8mud.com/100-series-c...pressomon.html |
| |
01-11-07, 04:34 PM
|
#6 (permalink)
| | Forum Lifer
Join Date: Dec 2003 Location: Rockville, MD
Posts: 2,758
| Technically you can't run them since the outlets are different according to amperage ratings.
However, my 220V stick welder's amp rating is far greater than the plug I have it plugged into. Why? I never come close to using my welder to it's full potential. If I exceed the circuit's capacity, the breaker simply trips. For home/hobby use, I don't see what the big deal is.
Ary
__________________ HOKIES UNITED Mobile Base Camp Trailer Build
Arya Ebrahimi
'94 FZJ80 220k miles, locked, 4.88s, 285 Revo's, ARB Bullbar, Hella 4000's, homemade drawers
'86 Toyota Pickup SAS'ed, welded, 4.88s, 38 TSLs, and lots o' tube |
| |
01-11-07, 04:50 PM
|
#7 (permalink)
| | Merchant of Death
Join Date: Mar 2003 Location: Gig Harbor WA
Posts: 12,101
| I run my 220v welder off my home dryer 220v 50amp plug and it works perfect
maybe Crusty TLC or Ziltch can chime in......
__________________ Truth is a torch that shines through the fog without dispelling it. Always be true to your work, your word, & your friends, & you will never live a day without peace
Last edited by Landpimp; 01-12-07 at 08:19 AM.
|
| |
01-11-07, 09:15 PM
|
#8 (permalink)
| | what he said
Join Date: Feb 2002 Location: Las Vegas
Posts: 13,493
| so is the power to your dryer 220 or 110??
What's the plug look like?
table saws and aircompressors are low amp draw tools.. welders are higher (depending on the welder)
My 220 compressor is 30 amp
my plasma cutter is 30 amp
My welder is 50 amp
__________________ I am kinda gay.......
I've set the bar, don't trip over it....
"Mary Poppins: In every job that must be done, there is an element of fun. You find the fun and - SNAP - the job's a game." |
| |
01-12-07, 08:22 AM
|
#9 (permalink)
| | 250+ Club
Join Date: Jan 2005 Location: Tulsa, OK
Posts: 476
| I have never seen a 100V electric dryer. If the circuit is 220V, it should have 2 breakers ganged together in the breaker box.
If that is the case, you can wire the welder to that outlet. If the welder draws over 30 amps, it will pop the breaker. The breaker is there to protect the wire. The wire size coming out of breaker box determine what size breaker is needed.
__________________ Dave Stinchcomb
Green Country Cruisers
1981 FJ60
1976 FJ40
1966 FJ40 |
| |
01-12-07, 11:36 AM
|
#10 (permalink)
| | Forum Regular
Join Date: Oct 2004
Posts: 216
| Quote:
Originally Posted by Okie_dave I have never seen a 100V electric dryer. If the circuit is 220V, it should have 2 breakers ganged together in the breaker box.
If that is the case, you can wire the welder to that outlet. If the welder draws over 30 amps, it will pop the breaker. The breaker is there to protect the wire. The wire size coming out of breaker box determine what size breaker is needed. | The dryer is 220v. It uses a dual 110/220 circuit because the timer and such on the dryer uses the lower voltage--at least that's my understanding. There is indeed a ganged 30 amp breaker on the circuit. It could easily be upgraded to a 50 amp--the wire is big enough to handle 50 amps at the length it runs now.
The plug is currently a typical 220v "appliance" type (three slots in a Y configuration). I initially asked the question because I was wondering if I could make a heavy duty adapter cord (a regular receptacle on one end with an appliance plug to matche the outlet on the other) so I could plug in a table saw, compressor, etc.--at least until I was able to run another line.
Timoss
88 fj62 TLCA |
| |
01-12-07, 12:40 PM
|
#11 (permalink)
| | Merchant of Death
Join Date: Mar 2003 Location: Gig Harbor WA
Posts: 12,101
| Tim, you can do exactaly what your planing. The darn plug ends(the dryer end) are about $20 though Quote:
Originally Posted by Timoss The dryer is 220v. It uses a dual 110/220 circuit because the timer and such on the dryer uses the lower voltage--at least that's my understanding. There is indeed a ganged 30 amp breaker on the circuit. It could easily be upgraded to a 50 amp--the wire is big enough to handle 50 amps at the length it runs now.
The plug is currently a typical 220v "appliance" type (three slots in a Y configuration). I initially asked the question because I was wondering if I could make a heavy duty adapter cord (a regular receptacle on one end with an appliance plug to matche the outlet on the other) so I could plug in a table saw, compressor, etc.--at least until I was able to run another line.
Timoss
88 fj62 TLCA |
__________________ Truth is a torch that shines through the fog without dispelling it. Always be true to your work, your word, & your friends, & you will never live a day without peace |
| |
01-12-07, 08:10 PM
|
#12 (permalink)
| | Site Addict
Join Date: Dec 2002 Location: Texas
Posts: 1,434
| Quote:
Originally Posted by Timoss The dryer is 220v. It uses a dual 110/220 circuit because the timer and such on the dryer uses the lower voltage--at least that's my understanding. There is indeed a ganged 30 amp breaker on the circuit. It could easily be upgraded to a 50 amp--the wire is big enough to handle 50 amps at the length it runs now.
The plug is currently a typical 220v "appliance" type (three slots in a Y configuration). I initially asked the question because I was wondering if I could make a heavy duty adapter cord (a regular receptacle on one end with an appliance plug to matche the outlet on the other) so I could plug in a table saw, compressor, etc.--at least until I was able to run another line.
Timoss
88 fj62 TLCA | Are you sure you can upgrade to a 50 amp breaker? I'm betting that the wire to the dryer is a 10 gauge. You'll need a 6 gauge for 50 amps.
Lots of guys have done what you're asking. I don't see any issues with it. Hard to mess up the wiring since you have 2 hots and 1 ground.
Depending on where you panel is located, it might be easy to run another circuit.
__________________ 69 FJ40 with some minor mods...
2000 Cummins powered Dodge with some power enhancements.
DO NOT SUPPORT TRAIL GEAR!!!!! bad ethics = bad business! http://www.paypalsucks.com |
| |
01-13-07, 07:18 AM
|
#13 (permalink)
| | Forum Lifer
Join Date: Mar 2003 Location: Sacramento, CA
Posts: 9,170
| My garage is on the backside of the utility room where the dryer is. SInce the dryer is gas, the 220 (actually 238V at my place) plug was not used. I opened up the wall on the garage side, pulled the wires through (they were 8 ga unfortunately), and installed a plug on the the garage side. I just matched the socket up with the welder plug. Technically the welder can draw above the 30amps of the circuit, but since I'm not building a battleship, I've never tripped it.
On the same circuit, I also ran another socket for the compressor which can draw 8-9 amps. I have sice learned this is not to code, and the plan is to take it out and have the garage wiring redone by a real electrician, with a subpanel, multiple 220 outlets, and more capacity. Still, It works, I'm just careful with my use patterns.
__________________ Andrew
1971 FJ-40 Rubicon tested, 2F powered, SM420, some mods
1976 FJ40 almost gone
1984 FJ-60 H41, Toybox, 4.56/ARBs, SOA, twin sticks and more
1989 FJ-62 125k-Stock, daily driver
1997 FZJ-80 Driveway queen, with door dent |
| |
01-17-07, 01:54 PM
|
#14 (permalink)
| | 250+ Club
Join Date: Nov 2006 Location: 6 Miles Past The Edge Of The World
Posts: 574
| Quote:
Originally Posted by fj40charles Are you sure you can upgrade to a 50 amp breaker? I'm betting that the wire to the dryer is a 10 gauge. You'll need a 6 gauge for 50 amps.
Lots of guys have done what you're asking. I don't see any issues with it. Hard to mess up the wiring since you have 2 hots and 1 ground.
Depending on where you panel is located, it might be easy to run another circuit. |
X2 on the wire size, if you go 50amp make sure you have 6 gauge wire or larger, if you over load small gauge wire with lots of amp you could burn something down.
__________________ 71 FJ55 - Project
52 Farmal Model 100
The Duty Is Ours, The Results Are God's.
- John Adams |
| |
02-06-07, 06:33 AM
|
#15 (permalink)
| | Focus on the Journey
Join Date: Jun 2005 Location: Southern Arizona
Posts: 1,460
| Quote:
Originally Posted by Cruiserdrew My garage is on the backside of the utility room where the dryer is. SInce the dryer is gas, the 220 (actually 238V at my place) plug was not used. I opened up the wall on the garage side, pulled the wires through (they were 8 ga unfortunately), and installed a plug on the the garage side. I just matched the socket up with the welder plug. Technically the welder can draw above the 30amps of the circuit, but since I'm not building a battleship, I've never tripped it.
On the same circuit, I also ran another socket for the compressor which can draw 8-9 amps. I have sice learned this is not to code, and the plan is to take it out and have the garage wiring redone by a real electrician, with a subpanel, multiple 220 outlets, and more capacity. Still, It works, I'm just careful with my use patterns. | 8 gage wire is rated at 40 amps. You could run that into a subpanel in the garage and install a 30 amp 220v service for your welder and a 15 amp 110v outlet for your compressor. Square D makes a breaker that has one 220v line and two 110v lines that only requires two breakeouts.
__________________ 78 FJ40
ARB's F&R, Rear Disks, DUI HEI, 200 Amp Alt, OME 2.5, 33x10.50, PS, RE8000, Stout Rear Bumper, 4+Plus Sliders/U-Bolt Flip Kit/Tie & Relay Rods/Anti-Inversion Shackles, Dual Tanks, BTB Dash Box, Tuned Ceramic Coated Headers, Extended Axle Vents, BrakeQuip Custom Certified SS Brake & Clutch Flex Lines ROTW My Yoda| HD Skid Plate| Recovery & Windshield Washer Tanks| Toyota Pulley on GM Pump| Bypass Hose| Vapor Recovery Tank |
| |
02-06-07, 12:49 PM
|
#16 (permalink)
| | Mod in Hibernation
Join Date: Sep 2004 Location: Where diesels purr and turbos whine
Posts: 6,320
| Most dryers run 220 and 110. The 110 is for the timer I guess. The 220 is for the coil.
Yes, 100% for sure you can use this outlet. Just buy a dryer plug. You only use the prongs that are 220. Do not use the forth prong.
I run my welder and my heater on this source. I made a 50 foot extension cable with the dryer plug on one end and the welder socket on the other. I also put a welder plug on my heater so I can just unplug one or the other.
__________________ -84 BJ60, Finally on the FN road!
-91 FJ80, wife's ride
Iron Butt award winner of the Cruise Moab 08 ! |
| |
02-06-07, 03:40 PM
|
#17 (permalink)
| | Forum Lifer
Join Date: Mar 2004 Location: Scottsdale Arizona
Posts: 3,964
| FWIW - The motor and timer/controls on a dryer is 110V only the heat is 220V
__________________ "Knowledge without experience is just information"--Mark Twain Copper State Cruisers #003 |
| |
02-06-07, 05:58 PM
|
#18 (permalink)
| | 250+ Club
Join Date: Apr 2004
Posts: 913
| Originally posted by OKI-DAVE:
220V is just 2 - 110V line 180* out of phase.
Actually in phase just opposite sides of a center tapped transformer, but in phase.. |
| |
02-09-07, 08:15 PM
|
#19 (permalink)
| | Forum Regular
Join Date: Sep 2003 Location: Magnolia, Arkansas
Posts: 141
| x2 on brew8's comment. Your entire house service is simply 2 lines of 110 (117) volts and a ground. When they enter the breaker box, they attach to non-adjacent lugs or taps---plug in a double breaker and you get 110 for each of the feed lines; therefore 220 volts.
Dryer IS a dedicated 220 volt line. The plug could be of a couple of designs, but the input into the dryer is 220v. Inside the dryer, the timer taps one of the wires for 110v; full 220v goes to heat element.
IF the outlet is not needed for dryer, why not simply pick up the correct 220v outlet at HD/Lowes to match your saws plug and replace the outlet on the wall. Trip the breaker, remove cover, remove and replace. No adapter needed. Follow the color code of the wires. The wire to the "pin" is the ground; the "blades" are each 110v. |
| |
02-09-07, 09:16 PM
|
#20 (permalink)
| | Supporting Vendor
Join Date: Jan 2003 Location: Cranbrook, B.C., Canada
Posts: 9,390
| A typical dryer plug has 4 wires. A neutral, a ground and TWO hot wires. You can run the saw or whatnot IF you use the correct two wires. The potential problem you have is that the saw is NOT protected by the dryer breaker as the saw is probably only rated at 8-10 amps. You'd need to overload the saw by 3 times!
Personally I would NOT recommend it simply for the safety of your tools.
Running a 220v circuit is not that difficult and then you could have the correct breaker and plugs.
Your home insurance may not look too kindly on your wiring handywork if an overloaded tool starts a fire!
__________________ '82 BJ60 H55 tranny, AXT turbo 3B diesel, high nickel alloy head, A/C, BDS lift, factory PTO, Aussie rear locker, OEM LSD front, 4:11's, 32's, PERFECT frame!
'76 FJ55, 3B turbo, alloy head, H41 tranny, 3 sp. transfer, 33's, A/C, PTO winch, long range tank!
'67 FJ45LV shop project c/w 3B turbo diesel transplant & H41 4 speed, 3 speed transfer, PTO! www.wirrell.com |