12-11-08, 04:11 PM
|
#1 | | Gubpimp 
Join Date: Mar 2003 Location: PNW
Posts: 12,251
| emergancy generator hookup to furnace Warning!
I aint in the mood to be preached at today....trust me its been a VERY bad week on a personal level, one of the worst ever.....so I just want to be able to provide heat for Connie and I if needed this winter if we have a major outage as we did 2 years ago(7 days)
See if this will work.
gas furnace, uses very little power, less than 15amps. Has its own breaker box.
Figured I could just cut the wires(3) between the breaker box and the furnace, then just install a male/female plugs like on an extention cord. When the power goes out, I just unplug the 2 ends, and plug the generator into the furance end and furance will work just like normal, its a brand new Trane gas furance
this should work right? cant see why it wont. 3 wires, black(power) green and white
yes my house is not wired proper for a generator but I have worked around that with no issues(even from the light company, who knows I do it like this) I just switch off the mains(in 2 places, inside and out) and backfeed the house thru the 230v unused drier outlet, but only some circuts work(like every other on the panel, funance is one that doesnt) but the stuff we need does, well pump, septic pump, good deal of lights etc. All we need is the furnace
and please no crap about how I do it, it can cuase NO harm(except maybe to me), even if the house somehow backfeed the mains the generator would trip as it was trying to backfeed the neighborhood and just overload in a mila second.
dad is doing pretty much the same, just going to power up the boiler for the floor radiant heat, to run their home would cost 20-30K for the correct set up(home as a commerical elevator in it) |
| |
12-11-08, 04:17 PM
|
#2 | | thursdays at 9:00
Join Date: Oct 2004 Location: Tannhauser Gate
Posts: 596
| Just shut the mains off and you're good to go...
__________________ avatar
"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski |
| |
12-11-08, 04:17 PM
|
#3 | | 250+ Club
Join Date: Aug 2005 Location: El Dorado County CA
Posts: 806
| It will work. As you wrote NOT to code. Insurance could deny you etc....
Purchase a good quality male / female connector.
Be careful when connecting it up in an outage.
Smoke detectors all installed, tested and in good working order.
__________________ 1977 FJ40 Softop
Chevy 350
Turbo 400
35 inch MTR's
Dual Band Ham
8274 with Synthetic rope
40 gallons on board fuel |
| |
12-11-08, 04:19 PM
|
#4 | | I've got a shark!
Join Date: Sep 2002 Location: with a fricken laser on its head!
Posts: 2,831
| Sounds okay.
Sorry you had a bad week.
__________________ "You cannot invade the mainland United States. There would be a rifle behind every blade of grass." -- Admiral Isoroku Yamamoto '99 UZJ100 "The Iron Hippo" / '82 FJ40 "Mustard" / '73 FJ40
'06 XT225 / '82 CT110 / '70 CT70"dude, I can't ban yooper....he's got friggin lazers on his head " -woody Quote:
Originally Posted by valentine Jesus, sometimes I'm such an idiot. | |
| |
12-11-08, 04:22 PM
|
#5 | | thursdays at 9:00
Join Date: Oct 2004 Location: Tannhauser Gate
Posts: 596
| Bad wiring will 99.99% of the time will go for a shit within the first hour or so of running. If you're a little paranoid, just go and check on it a couple of times during the first 90mins or so. Warm wires, OK. Hot, like burn your finger hot, bad.
Feel free to vent, if you want...
__________________ avatar
"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski
Last edited by Chang-kuao-lo; 12-11-08 at 04:23 PM.
Reason: oh, no reason
|
| |
12-11-08, 04:32 PM
|
#6 | | Site Addict
Join Date: May 2005 Location: West Palm Beach, Florida
Posts: 1,864
| Sounds like you've got a 110 volt generator. Thats why only every-other circuit works when you back-feed the dryer outlet. Most likely, your blower motor on your heater is 220 volt. Check it out first. If it is 220 volt, you will need a 220 volt generator feed.
__________________ Capt. Jim
Florida Land Cruiser Association
North Florida Cruiserheads
Upstate Cruisers
TLCA #5390 |
| |
12-11-08, 04:45 PM
|
#7 | | thursdays at 9:00
Join Date: Oct 2004 Location: Tannhauser Gate
Posts: 596
| If the furnace is 220V, there will be two "hot" wires, ie green(ground), black(hot 110V), white(common), red(hot 110V). The breaker for the furnace will tell you if it's 110 or 220. 220 will occupy two slots on the load centre.
__________________ avatar
"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski |
| |
12-11-08, 06:42 PM
|
#8 | | northern latecomer 
Join Date: Mar 2003 Location: north of 49
Posts: 4,504
| if it is 220v you also should use a 220 volt plug set instead of regular plug.
running lumex wire directly from a breaker box to a female extension cord plug connector is pretty egregiously mickey mouse but i guess it will work.
you can get this closer to code and much safer pretty cheaply
get some 20 amp dryer wire and wire it to the connectors on your furnace where the lumex ends now and attach a proper male plug (220 or 110) to the other end.
-buy an external mount interior single gang junction box and screw or nail it to the wall near the furnace
-put the correct plug in it and run your lumex wire from the breaker box into that junction box and onto the plug and ground it while you are at it.
-put a face plate on for good measure
this is about $40 worth of stuff
__________________ 93 fzj80
66 fj40L
m101cdn trailer
91 LS400 sedancruiser
64, 2x65 honda ct 200
67, 2x68, 3x69, 72, 75 Honda ct90
83 Honda ct70
48 Ferguson TE20
"Diplomacy is the art of having someone else impose your will on you" Lester Pearson
"I have the conch" Piggy wfc 4812-2635-4880 |
| |
12-11-08, 06:45 PM
|
#9 | | Reintarnated 
Join Date: Feb 2005 Location: Victopia BC
Posts: 605
| You should really install a transfer switch. Not hard to do, and it would be safer.
__________________ imagine: a world where slower drivers kept right |
| |
12-11-08, 06:46 PM
|
#10 | | 250+ Club
Join Date: Jul 2006 Location: hillbilly desert rat
Posts: 508
| just make sure you use a SO or SJ cord for this hook up .. this grade of wire has better insulation on it and is a softer copper. I lived in Hurricane country for years and that is the way I did it. I am a elect by trade. Just do not use electronics or a tv you care about.
__________________ 91 running 33 toyo mt's hillbilly roof rack,air lockers,Tube bumper,breaking stuff too.. custom dog tags for sale GI style or for pets $5 includes shipping
I don't give a damn for a man that can only spell a word one way.
decavo's custom jewelry ,vegan soaps, lip balm, lotions all natural products |
| |
12-11-08, 06:52 PM
|
#11 | | At the Tannhäuser Gate
Join Date: Sep 2008 Location: Houston, Texas
Posts: 1,441
| Quote:
Originally Posted by semlin if it is 220v you also should use a 220 volt plug set instead of regular plug.
running lumex wire directly from a breaker box to a female extension cord plug connector is pretty egregiously mickey mouse but i guess it will work.
you can get this closer to code and much safer pretty cheaply
get some 20 amp dryer wire and wire it to the connectors on your furnace where the lumex ends now and attach a proper male plug (220 or 110) to the other end.
-buy an external mount interior single gang junction box and screw or nail it to the wall near the furnace
-put the correct plug in it and run your lumex wire from the breaker box into that junction box and onto the plug and ground it while you are at it.
-put a face plate on for good measure
this is about $40 worth of stuff | i did something similar to the main at my house.
I was getting prepared for Ike, and wanted to run as much of the house as possible when we lost power. Various Images from my Ike Adventure
With this I could run everything in the house on a 5500/8500 generator EXCEPT the AC, the electric dryer, and the microwave. (The damn microwave took 25 amps by itself)
We had power in the house within 15 min of losing utility power.
as soon as we lost service, we disconnected the service main, removed the neutral leg, flipped the small disconnect, and plugged in the generator.
worked great. Saved $800 over going with an auto-switch.
__________________ Stop Sheila Jackson Lee Now! Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it. Quote:
Originally Posted by titanpat57 If bpassmore said it, I believe it, and that's final... | "Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas
1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly. LX Clading and Flares for sale |
| |
12-11-08, 07:52 PM
|
#12 | | 250+ Club 
Join Date: Oct 2006 Location: Columbus, OH
Posts: 592
| I got Amazon.com: Reliance Controls PB30 30 Amp Power Inlet Box: Home Improvement and an NEM L14 power cord. I wired the power inlet box to a 40 amp breaker in the box. Just make sure the breaker is turnd off when not using and the main breaker is off when backfeeding
__________________ 1997 LX450 Green! with lockers
2006 GX470 for the |
| |
12-11-08, 07:56 PM
|
#13 | | At the Tannhäuser Gate
Join Date: Sep 2008 Location: Houston, Texas
Posts: 1,441
| Quote:
Originally Posted by john_eckels Just make sure the breaker is turnd off when not using and the main breaker is off when backfeeding |
this is not enough. the neutral bar can and will still carry current even when the main is disconnected.
when i setup my disconnect panel, i tested voltage across the busses after main disconnect. i found that my (fairly new and well built house) wiring allowed for bleed through back to the common (neutral) bar.
be sure to switch off the main, and manually disconnect the neutral buss when doing this.
I use a dual pole 60 amp breaker in my main panel and fed into that.
__________________ Stop Sheila Jackson Lee Now! Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it. Quote:
Originally Posted by titanpat57 If bpassmore said it, I believe it, and that's final... | "Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas
1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly. LX Clading and Flares for sale
Last edited by bpassmore; 12-11-08 at 08:31 PM.
|
| |
12-11-08, 07:57 PM
|
#14 | | At the Tannhäuser Gate
Join Date: Sep 2008 Location: Houston, Texas
Posts: 1,441
| Quote:
Originally Posted by john_eckels | that is what I have pictured in the link above.
here is a closer image
__________________ Stop Sheila Jackson Lee Now! Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it. Quote:
Originally Posted by titanpat57 If bpassmore said it, I believe it, and that's final... | "Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas
1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly. LX Clading and Flares for sale |
| |
12-12-08, 07:45 AM
|
#15 | | Gubpimp 
Join Date: Mar 2003 Location: PNW
Posts: 12,251
| Jim, we talked about this 2 years ago when I was without power for 7 days, you gave me good ideas then
my furnace is 110 and gas, it just needs to power the fan and circut board, it runs on less than 15 amps(as thats the breaker it comes off)
my generator is 220/110
its the way my panel is wired(I thought it was you that explained it to me) as to why every other circut works, as my well pump is 220v and it runs fine when I backfeed the house
I have two discounects, one right at the meter and one at the main panel in the house, the lineman from the power company actaully checked it for me last storm and no power was feeding to the main lines Quote:
Originally Posted by Capt. Jim Sounds like you've got a 110 volt generator. Thats why only every-other circuit works when you back-feed the dryer outlet. Most likely, your blower motor on your heater is 220 volt. Check it out first. If it is 220 volt, you will need a 220 volt generator feed. | |
| |
12-12-08, 07:46 AM
|
#16 | | Gubpimp 
Join Date: Mar 2003 Location: PNW
Posts: 12,251
| BTW......thanks for not preaching.....Ill let ya all beat me up latter |
| |
12-12-08, 07:48 AM
|
#17 | | 250+ Club
Join Date: Jul 2004 Location: Olympia, WA
Posts: 879
| John, sorry to hear that you're having a bad week. I'm getting the generator ready as well. It sounds like we're in for quite a storm. I don't know about Gig Harbor but here in Olympia we usually get a load of bad weather when it goes to s**t. Good luck!
__________________ Doug
Olympia WA 1977 FJ40
1968 R60/2 W/Steib S350
1980 CT110
2009 KLR 650E9 |
| |
12-12-08, 07:59 AM
|
#18 | | what did I do now?
Join Date: Feb 2006
Posts: 10,908
| Surge protection for the board in your furnace which you need anyway.
__________________ NEW! Club sticker for sale. pm me for details! MountaineerCruisers.net
Originally Posted by monniepoo I got attacked repeatedly by a trouser snake |
| |
12-12-08, 07:59 AM
|
#19 | | Forum Lifer
Join Date: Dec 2002 Location: buggerville nj
Posts: 6,043
| Quote:
Originally Posted by Landpimp BTW......thanks for not preaching.....Ill let ya all beat me up latter  | Ok, it's been long enough.
You fuckless wonder.
Sorry you had a bad week man. |
| |
12-12-08, 08:59 AM
|
#20 | | Site Addict
Join Date: May 2006 Location: erie pa
Posts: 1,749
| being a lineman for a few years the biggest problem with generators is they back feed and the line man get hurt.the way you plan to do it is simple and cant back feed with the furnace unplluged and plugged into the generator. just use the proper plugs and correct wire size.and you will be good .
__________________ 64,65,69,69,70,73,77 fj40s wagon and pickup sold |
| |  | |