emergancy generator hookup to furnace

Warning!
I aint in the mood to be preached at today....trust me its been a VERY bad week on a personal level, one of the worst ever.....so I just want to be able to provide heat for Connie and I if needed this winter if we have a major outage as we did 2 years ago(7 days)

See if this will work.

gas furnace, uses very little power, less than 15amps. Has its own breaker box.

Figured I could just cut the wires(3) between the breaker box and the furnace, then just install a male/female plugs like on an extention cord. When the power goes out, I just unplug the 2 ends, and plug the generator into the furance end and furance will work just like normal, its a brand new Trane gas furance

this should work right? cant see why it wont. 3 wires, black(power) green and white

yes my house is not wired proper for a generator but I have worked around that with no issues(even from the light company, who knows I do it like this) I just switch off the mains(in 2 places, inside and out) and backfeed the house thru the 230v unused drier outlet, but only some circuts work(like every other on the panel, funance is one that doesnt) but the stuff we need does, well pump, septic pump, good deal of lights etc. All we need is the furnace

and please no crap about how I do it, it can cuase NO harm(except maybe to me), even if the house somehow backfeed the mains the generator would trip as it was trying to backfeed the neighborhood and just overload in a mila second.

dad is doing pretty much the same, just going to power up the boiler for the floor radiant heat, to run their home would cost 20-30K for the correct set up(home as a commerical elevator in it)
Landpimp is offline   Reply With Quote
Old 12-11-08, 04:17 PM   #2
thursdays at 9:00


 
Chang-kuao-lo's Avatar
 
Join Date: Oct 2004
Location: Tannhauser Gate
Posts: 596
Just shut the mains off and you're good to go...

__________________
avatar

"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski
Chang-kuao-lo is offline   Reply With Quote
Sponsor 12-11-08, 04:17 PM
Sponsored Link
advertisement
Old 12-11-08, 04:17 PM   #3
250+ Club


 
FJ40_owner's Avatar
 
Join Date: Aug 2005
Location: El Dorado County CA
Posts: 806
It will work. As you wrote NOT to code. Insurance could deny you etc....

Purchase a good quality male / female connector.

Be careful when connecting it up in an outage.

Smoke detectors all installed, tested and in good working order.

__________________
1977 FJ40 Softop
Chevy 350
Turbo 400
35 inch MTR's
Dual Band Ham
8274 with Synthetic rope
40 gallons on board fuel
FJ40_owner is offline   Reply With Quote
Old 12-11-08, 04:19 PM   #4
I've got a shark!


 
yooper's Avatar
 
Join Date: Sep 2002
Location: with a fricken laser on its head!
Posts: 2,831
Sounds okay.

Sorry you had a bad week.

__________________
"You cannot invade the mainland United States. There would be a rifle behind every blade of grass." -- Admiral Isoroku Yamamoto
'99 UZJ100 "The Iron Hippo" / '82 FJ40 "Mustard" / '73 FJ40
'06 XT225 / '82 CT110 / '70 CT70
"dude, I can't ban yooper....he's got friggin lazers on his head " -woody


Quote:
Originally Posted by valentine View Post
Jesus, sometimes I'm such an idiot.
yooper is online now   Reply With Quote
Old 12-11-08, 04:22 PM   #5
thursdays at 9:00


 
Chang-kuao-lo's Avatar
 
Join Date: Oct 2004
Location: Tannhauser Gate
Posts: 596
Bad wiring will 99.99% of the time will go for a shit within the first hour or so of running. If you're a little paranoid, just go and check on it a couple of times during the first 90mins or so. Warm wires, OK. Hot, like burn your finger hot, bad.


Feel free to vent, if you want...

__________________
avatar

"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski

Last edited by Chang-kuao-lo; 12-11-08 at 04:23 PM. Reason: oh, no reason
Chang-kuao-lo is offline   Reply With Quote
Old 12-11-08, 04:32 PM   #6
Site Addict


 
Capt. Jim's Avatar
 
Join Date: May 2005
Location: West Palm Beach, Florida
Posts: 1,864
Sounds like you've got a 110 volt generator. Thats why only every-other circuit works when you back-feed the dryer outlet. Most likely, your blower motor on your heater is 220 volt. Check it out first. If it is 220 volt, you will need a 220 volt generator feed.

__________________
Capt. Jim
Florida Land Cruiser Association
North Florida Cruiserheads
Upstate Cruisers
TLCA #5390
Capt. Jim is offline   Reply With Quote
Old 12-11-08, 04:45 PM   #7
thursdays at 9:00


 
Chang-kuao-lo's Avatar
 
Join Date: Oct 2004
Location: Tannhauser Gate
Posts: 596
If the furnace is 220V, there will be two "hot" wires, ie green(ground), black(hot 110V), white(common), red(hot 110V). The breaker for the furnace will tell you if it's 110 or 220. 220 will occupy two slots on the load centre.

__________________
avatar

"have a crappy weekend, i hope your house burns down."
-carl brutananadilewski
Chang-kuao-lo is offline   Reply With Quote
Old 12-11-08, 06:42 PM   #8
northern latecomer

semlin supports the BlueRibbon Coalition!
 
semlin's Avatar
 
Join Date: Mar 2003
Location: north of 49
Posts: 4,504
if it is 220v you also should use a 220 volt plug set instead of regular plug.

running lumex wire directly from a breaker box to a female extension cord plug connector is pretty egregiously mickey mouse but i guess it will work.

you can get this closer to code and much safer pretty cheaply

get some 20 amp dryer wire and wire it to the connectors on your furnace where the lumex ends now and attach a proper male plug (220 or 110) to the other end.

-buy an external mount interior single gang junction box and screw or nail it to the wall near the furnace

-put the correct plug in it and run your lumex wire from the breaker box into that junction box and onto the plug and ground it while you are at it.

-put a face plate on for good measure

this is about $40 worth of stuff

__________________
93 fzj80
66 fj40L
m101cdn trailer
91 LS400 sedancruiser
64, 2x65 honda ct 200
67, 2x68, 3x69, 72, 75 Honda ct90
83 Honda ct70
48 Ferguson TE20
"Diplomacy is the art of having someone else impose your will on you" Lester Pearson

"I have the conch" Piggy
wfc 4812-2635-4880
semlin is offline   Reply With Quote
Old 12-11-08, 06:45 PM   #9
Reintarnated

Red Herring supports the BlueRibbon Coalition!
 
Red Herring's Avatar
 
Join Date: Feb 2005
Location: Victopia BC
Posts: 605
You should really install a transfer switch. Not hard to do, and it would be safer.

__________________
imagine: a world where slower drivers kept right
Red Herring is offline   Reply With Quote
Old 12-11-08, 06:46 PM   #10
250+ Club


 
decavo's Avatar
 
Join Date: Jul 2006
Location: hillbilly desert rat
Posts: 508
just make sure you use a SO or SJ cord for this hook up .. this grade of wire has better insulation on it and is a softer copper. I lived in Hurricane country for years and that is the way I did it. I am a elect by trade. Just do not use electronics or a tv you care about.

__________________
91 running 33 toyo mt's hillbilly roof rack,air lockers,Tube bumper,breaking stuff too..


custom dog tags for sale GI style or for pets $5 includes shipping

I don't give a damn for a man that can only spell a word one way.


decavo's custom jewelry ,vegan soaps, lip balm, lotions all natural products
decavo is offline   Reply With Quote
Old 12-11-08, 06:52 PM   #11
At the Tannhäuser Gate


 
bpassmore's Avatar
 
Join Date: Sep 2008
Location: Houston, Texas
Posts: 1,441
Garage
Quote:
Originally Posted by semlin View Post
if it is 220v you also should use a 220 volt plug set instead of regular plug.

running lumex wire directly from a breaker box to a female extension cord plug connector is pretty egregiously mickey mouse but i guess it will work.

you can get this closer to code and much safer pretty cheaply

get some 20 amp dryer wire and wire it to the connectors on your furnace where the lumex ends now and attach a proper male plug (220 or 110) to the other end.

-buy an external mount interior single gang junction box and screw or nail it to the wall near the furnace

-put the correct plug in it and run your lumex wire from the breaker box into that junction box and onto the plug and ground it while you are at it.

-put a face plate on for good measure

this is about $40 worth of stuff
i did something similar to the main at my house.
I was getting prepared for Ike, and wanted to run as much of the house as possible when we lost power.

Various Images from my Ike Adventure









With this I could run everything in the house on a 5500/8500 generator EXCEPT the AC, the electric dryer, and the microwave. (The damn microwave took 25 amps by itself)

We had power in the house within 15 min of losing utility power.

as soon as we lost service, we disconnected the service main, removed the neutral leg, flipped the small disconnect, and plugged in the generator.

worked great. Saved $800 over going with an auto-switch.

__________________
Stop Sheila Jackson Lee Now!

Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it.

Quote:
Originally Posted by titanpat57 View Post
If bpassmore said it, I believe it, and that's final...
"Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas

1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly.
LX Clading and Flares for sale
bpassmore is offline   Reply With Quote
Old 12-11-08, 07:52 PM   #12
250+ Club

john_eckels supports the BlueRibbon Coalition!
 
john_eckels's Avatar
 
Join Date: Oct 2006
Location: Columbus, OH
Posts: 592
I got Amazon.com: Reliance Controls PB30 30 Amp Power Inlet Box: Home Improvement and an NEM L14 power cord. I wired the power inlet box to a 40 amp breaker in the box. Just make sure the breaker is turnd off when not using and the main breaker is off when backfeeding

__________________
1997 LX450 Green! with lockers
2006 GX470 for the
john_eckels is online now   Reply With Quote
Old 12-11-08, 07:56 PM   #13
At the Tannhäuser Gate


 
bpassmore's Avatar
 
Join Date: Sep 2008
Location: Houston, Texas
Posts: 1,441
Garage
Quote:
Originally Posted by john_eckels View Post
Just make sure the breaker is turnd off when not using and the main breaker is off when backfeeding

this is not enough. the neutral bar can and will still carry current even when the main is disconnected.

when i setup my disconnect panel, i tested voltage across the busses after main disconnect. i found that my (fairly new and well built house) wiring allowed for bleed through back to the common (neutral) bar.

be sure to switch off the main, and manually disconnect the neutral buss when doing this.

I use a dual pole 60 amp breaker in my main panel and fed into that.

__________________
Stop Sheila Jackson Lee Now!

Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it.

Quote:
Originally Posted by titanpat57 View Post
If bpassmore said it, I believe it, and that's final...
"Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas

1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly.
LX Clading and Flares for sale

Last edited by bpassmore; 12-11-08 at 08:31 PM.
bpassmore is offline   Reply With Quote
Old 12-11-08, 07:57 PM   #14
At the Tannhäuser Gate


 
bpassmore's Avatar
 
Join Date: Sep 2008
Location: Houston, Texas
Posts: 1,441
Garage
Quote:
Originally Posted by john_eckels View Post
that is what I have pictured in the link above.

here is a closer image

__________________
Stop Sheila Jackson Lee Now!

Tell a man that there are 400 billion stars and he'll believe you. Tell him a bench has wet paint and he has to touch it.

Quote:
Originally Posted by titanpat57 View Post
If bpassmore said it, I believe it, and that's final...
"Restriction on free thought and free speech is the most dangerous of all subversions. It is the one un-American act that could most easily defeat us." - William Douglas

1997 LX450, Rhinolined, 3x Locked, 315s, Pin7, Tacoma DC shaft, some neat stuff. more stuff needed.
2003 Ford Failstar. Wheel chair friendly.
LX Clading and Flares for sale
bpassmore is offline   Reply With Quote
Old 12-12-08, 07:45 AM   #15
Gubpimp

Landpimp supports the BlueRibbon Coalition!
 
Landpimp's Avatar
 
Join Date: Mar 2003
Location: PNW
Posts: 12,251
Jim, we talked about this 2 years ago when I was without power for 7 days, you gave me good ideas then

my furnace is 110 and gas, it just needs to power the fan and circut board, it runs on less than 15 amps(as thats the breaker it comes off)

my generator is 220/110

its the way my panel is wired(I thought it was you that explained it to me) as to why every other circut works, as my well pump is 220v and it runs fine when I backfeed the house

I have two discounects, one right at the meter and one at the main panel in the house, the lineman from the power company actaully checked it for me last storm and no power was feeding to the main lines

Quote:
Originally Posted by Capt. Jim View Post
Sounds like you've got a 110 volt generator. Thats why only every-other circuit works when you back-feed the dryer outlet. Most likely, your blower motor on your heater is 220 volt. Check it out first. If it is 220 volt, you will need a 220 volt generator feed.
Landpimp is offline   Reply With Quote
Old 12-12-08, 07:46 AM   #16
Gubpimp

Landpimp supports the BlueRibbon Coalition!
 
Landpimp's Avatar
 
Join Date: Mar 2003
Location: PNW
Posts: 12,251
BTW......thanks for not preaching.....Ill let ya all beat me up latter
Landpimp is offline   Reply With Quote
Old 12-12-08, 07:48 AM   #17
250+ Club


 
Doug_S's Avatar
 
Join Date: Jul 2004
Location: Olympia, WA
Posts: 879
John, sorry to hear that you're having a bad week. I'm getting the generator ready as well. It sounds like we're in for quite a storm. I don't know about Gig Harbor but here in Olympia we usually get a load of bad weather when it goes to s**t. Good luck!

__________________
Doug
Olympia WA

1977 FJ40
1968 R60/2 W/Steib S350
1980 CT110
2009 KLR 650E9
Doug_S is offline   Reply With Quote
Old 12-12-08, 07:59 AM   #18
what did I do now?


 
cruiser88's Avatar
 
Join Date: Feb 2006
Posts: 10,908
Surge protection for the board in your furnace which you need anyway.

__________________
NEW! Club sticker for sale. pm me for details!
MountaineerCruisers.net

Originally Posted by monniepoo I got attacked repeatedly by a trouser snake
cruiser88 is offline   Reply With Quote
Old 12-12-08, 07:59 AM   #19
Forum Lifer


 
Junk's Avatar
 
Join Date: Dec 2002
Location: buggerville nj
Posts: 6,043
Quote:
Originally Posted by Landpimp View Post
BTW......thanks for not preaching.....Ill let ya all beat me up latter
Ok, it's been long enough.

You fuckless wonder.

Sorry you had a bad week man.
Junk is offline   Reply With Quote
Old 12-12-08, 08:59 AM
Sponsored Link
advertisement
Old 12-12-08, 08:59 AM   #20
Site Addict


 
shelfboy1's Avatar
 
Join Date: May 2006
Location: erie pa
Posts: 1,749
being a lineman for a few years the biggest problem with generators is they back feed and the line man get hurt.the way you plan to do it is simple and cant back feed with the furnace unplluged and plugged into the generator. just use the proper plugs and correct wire size.and you will be good .

__________________
64,65,69,69,70,73,77 fj40s wagon and pickup sold
shelfboy1 is offline   Reply With Quote
Reply

Bookmarks




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On




All times are GMT -7. The time now is 07:02 PM.


vBulletin® v3.8.4 ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.2
Clubs, Garage Plus, Vendor Tools vBulletin Plugins by Drive Thru Online, Inc.
©2000-2010 by IH8MUD.com - ALL RIGHTS RESERVED